Page 1 of 1

JLD612 ssr voltage too low

Posted: Fri Feb 25, 2011 8:34 pm
by Bangalore
I have everything set up correctly, but my multimeter reads only .5 vdc from the ssr pins on the JLD612. I believe it is defective. Any ideas?

Re: JLD612 ssr voltage too low

Posted: Fri Feb 25, 2011 10:32 pm
by Tech_Marco
Not necessary. It depends on the stages of the controller is running. If PV and SV is getting very closed, the output is very low from 0, 0.5V, 1V... bouncing up and down and LED blink. But if SV is far from the PV, there is almost a DC 6V (not 8V) output from the controller's SSR output pins. You can use the arrow kep to set the SV higher than the PV and the LED (Out) should be constantly On instead of blinking. The output should be around 6V in this case. Try it

Re: JLD612 ssr voltage too low

Posted: Fri Feb 25, 2011 11:08 pm
by Bangalore
Unfortunately, no, even with the sv set at over 200 degrees above the pv, I still get no more than 1.5 vdc from pins 6&7 (the ssr out pins). The out light is solid on but no increase in voltage. Fortunately it is brand new. I have sent a request for a replacement.

Re: JLD612 ssr voltage too low

Posted: Sat Feb 26, 2011 12:11 am
by Tech_Marco
What is the output mode you configured the controller, 0,1,2,3,4 ?
Choose 2 for SSR

If it's still not working, sure you can send it back for exchange.

Re: JLD612 ssr voltage too low

Posted: Sat Feb 26, 2011 6:11 am
by Bangalore
Yes, it was 2. Thank you.