Urgent help needed JLD7100

Post Reply
doghouse
Posts: 1
Joined: Mon Dec 20, 2010 1:16 pm
Contact:

Urgent help needed JLD7100

Post by doghouse »

Hello. I need some help, please, setting up this controller. i have a type "J" thermocouple and am using the relay output. I want a simple on off control to drive a .5A pump. On at 130 degress F and off at 140 degrees F. I cannot seep to find out how to get the controller to do this. Any help is greatly appreciated. Thanks.
Tech_Marco
Posts: 4649
Joined: Mon Jun 15, 2009 3:00 pm
Contact:

Re: Urgent help needed JLD7100

Post by Tech_Marco »

1) Prgram the controller for "J" thermocouple
2) Set output mode "Inty" to 1
3) Connect your fan the the relay "J1" in series so that hte relay can control it On or Off

If you can't get the P,I,D working properly, may be you should use the "Auto" to tune the the PID parameters but it may take as short as mintues to as long as hours to complete the tuning.

Please read through the manual and see the example below of that

Marco