416PVA meter current transformers

Posted: Tue May 29, 2012 9:32 am
by tigersmith
Greetings,
I recently received a 416PVA 3 phase power meter. The current transformers I plan to use with this meter are rated: 400A : 0.333V. Will these work?
George

Re: 416PVA meter current transformers

Posted: Wed May 30, 2012 11:56 am
by Tech_Marco
Hello George:

First of all, the JLD416PVA is a single phase AC power meter, not 3 phase. You need three if you want to monitor 3 phase power supply. Also, "400A : 0.333V" sounds odd to me. It should be ratio on current but not ratio on current vs voltage. The 400A C.T. should be something sounds like "400A:5A" or "80:1". It make more sense.

Without the ratio info, it's not possible to configure the meter to read data correctly. It need ratio in integer number. If you're not sure, may be you should get one of our C.T. like the one 500A: 5A (100:1)


Marco

Re: 416PVA meter current transformers

Posted: Wed May 30, 2012 12:22 pm
by tigersmith
My bad....The 416PVA is one I was going to get for home use. The one I got for work was the JLD3300.
Further research shows the CT's I mentioned will not work. I have the correct 400:5 CT's on the way.

George