JLD612 Problem
-
- Posts: 1
- Joined: Thu Dec 29, 2011 12:07 pm
- Contact:
JLD612 Problem
So, I am using a JLD612, along with a P100 controller and SSR. The controller seems to be working fine, but it reads 5F low. In other words, if I set the controller to 100F, the actual temp will be 105F. It's as easy fix to set the Psb to +5, but then the controller overruns the PV by the same 5F.
-
- Posts: 270
- Joined: Mon Jan 03, 2011 3:47 pm
- Contact:
Re: JLD612 Problem
So when the controller is at equilibrium, if the SV = 100, the PV = 105?
Try setting the PSb to -5, which I think doesn't recalibrate the sensor but adjusts the controller offset.
Worth a try.
Try setting the PSb to -5, which I think doesn't recalibrate the sensor but adjusts the controller offset.
Worth a try.