Large temperature offset with JLD612DC and thermocouples

Post Reply
[email protected]
Posts: 4
Joined: Fri Nov 25, 2011 9:41 am
Contact:

Large temperature offset with JLD612DC and thermocouples

Post by [email protected] »

I recently purchased a JLD612 and I am having trouble with the temperature readings. When I attach a type t thermocouple I get a PV reading of -14C in ice water, 3C at room temperature of 19C (measured with a thermometer), and 20 when placed in a 37C incubator. When I use a type k thermocouple I get -12C in ice water, 6C at room temperature of 19C, and 17C in the 37C incubator. I have checked the thermocouples on my data logger and they work fine (+/- 2C). I have double checked the intY setting (t for type t and backwards 4 for type k) and even tried reversing the leads of the thermocouples. With the type t thermocouple I can sort of calibrate the error out with PSb even though the offsets range for 14C to 17C but the coefficients for the type k range from 12C to 20C. I am not sure what else to check at this point. I have read in one of the other posts that offsets shouldn't be that large, though in that case the problem was traced back to a defective thermocouple.
richiem
Posts: 270
Joined: Mon Jan 03, 2011 3:47 pm
Contact:

Re: Large temperature offset with JLD612DC and thermocouples

Post by richiem »

Seems like it could only be one of two problems:
1) the thermocouples are hooked up to the wrong terminals
2) the JLD612 is bad
[email protected]
Posts: 4
Joined: Fri Nov 25, 2011 9:41 am
Contact:

Re: Large temperature offset with JLD612DC and thermocouples

Post by [email protected] »

My first thought was the thermocouple leads were reversed so I swapped them and the sensed temperature went up when it should have gone down.