Jld612 doesn't turn off completely

Post Reply
Redblackviper
Posts: 3
Joined: Tue Mar 08, 2011 10:33 am
Contact:

Jld612 doesn't turn off completely

Post by Redblackviper »

I have two 2200 watt heaters 220v ac, I bought 2 jld612 and 2 40amp ssr.
The jld612 works turns the heaters on and gets up to the 130f required temp but it starts blinking after it passes the 130f mark AND the temp slowly rises it slowly rose to 150f I can't have it run that high. Seams like the ssr is working good I Also have two aluminum heat sinks and a cooling fan.
Also I have a k type thermo coupler
richiem
Posts: 270
Joined: Mon Jan 03, 2011 3:47 pm
Contact:

Re: Jld612 doesn't turn off completely

Post by richiem »

One possible thing comes to mind -- that you didn't program the JLD612 for the K type thermocouple -- the 612 is set by default for the Pt100 RTD from the factory.
Tech_Marco
Posts: 4647
Joined: Mon Jun 15, 2009 3:00 pm
Contact:

Re: Jld612 doesn't turn off completely

Post by Tech_Marco »

Blanking means the SSR change stages from fully ON to partially On. It's good sign that he controller and the SSR is functioning. It's just a matter of PID setting that it's over-shooting. Try use "AT" to let the controller to do auto tuning for the PID parameters