JLD612/PT100 EEEE

Post by x2b »

I ordered the JLD612 and the the PT-100. I can't get the controller to show anything but EEEE (or EEE.E). I hooked the red wire to terminal 10 and the two blue wires to terminals 8 and 9 (actually, I tried all permutations). I set IntY to P100 (and also tried P10.0).
The only thing that does seem to somewhat work is setting IntY to K (at that point the PV value shows something that seems correct).

Am I doing something wrong or do I just have a defective PT100?
Tech_Marco
Posts: 4646
Joined: Mon Jun 15, 2009 3:00 pm
Contact:

Re: JLD612/PT100 EEEE

Post by Tech_Marco »

Red to #8 and two blue to #9 and #10
Make sure that you're configure the controller for "PT10.0"
x2b
Posts: 4
Joined: Sat Mar 12, 2011 8:13 pm
Contact:

Re: JLD612/PT100 EEEE

Post by x2b »

Thanks Marco.

Tried that as one of the permutations before, and just tried it again. Same results.
Tech_Marco
Posts: 4646
Joined: Mon Jun 15, 2009 3:00 pm
Contact:

Re: JLD612/PT100 EEEE

Post by Tech_Marco »

I think the problem is faulty probe. Do you have another probe that you can give a try?
x2b
Posts: 4
Joined: Sat Mar 12, 2011 8:13 pm
Contact:

Re: JLD612/PT100 EEEE

Post by x2b »

Thanks Marco. I send a note to contactus to understand how I get it replaced.
x2b
Posts: 4
Joined: Sat Mar 12, 2011 8:13 pm
Contact:

Re: JLD612/PT100 EEEE

Post by x2b »

Just received the replacement probe. Problem resolved. Thanks!
ClarencePJ
Posts: 1
Joined: Sat Feb 14, 2015 3:04 am
Contact:

Re: JLD612/PT100 EEEE

Post by ClarencePJ »

Reddish colored in order to #8 as well as a couple of azure in order to #9 as well as #10
Make certain that you happen to be configure the controller intended for "PT10. 0".







______________________________________________________________________________________
http://www.realtests.com/
Post Reply

Return to “Temperature Controller”

Who is online

Users browsing this forum: No registered users and 7 guests