Post by dovaleh »

Hi,
I bought the 612 and starting to hook it up.
the K type TC works fine
but a pt100 shows EEEE
I checked the resistance of the pt100 and it is 115 ohm
any idea?
which terminal connection should i use?
thanks
Last edited by dovaleh on Fri Oct 22, 2010 9:45 am, edited 1 time in total.
dovaleh
Posts: 2
Joined: Thu Oct 21, 2010 1:33 pm
Contact:

Re: PT100 connection problem

Post by dovaleh »

just found the solution:
from http://www.jimsbeerkit.com/forum/viewto ... &sk=t&sd=a

connected the 2 wire pt100 to 8 and 9, and also connected 9 and 10

best

dov