JLD612 & PT100 ??
Posted: Sat Apr 02, 2016 7:39 am
The problem I’m having is with the psb offset which is -79°
I checked the offset with a Omega digital thermometer.
The PT100 read 101.2 ohms @ .2c and 134.1 ohms @ 100c
I removed the PT100 from the oven and inserted the tip in boiling water, the JLD612 showed 204 ° while my Omega showed 210.6° ???
Inty = P100
Outy = 2
Hy = 003
Psb = -79
Rd = 0
Corf = 1
Run AT and this is what I have
{NOTE I changed the Souf .02 to .05 as it was over shooting the sv set at 400°}
0036
P = 5.2
I = 0156
d = 039
Souf = .02
Oe = 002
File =0
Thanks